Author Topic: electrical question  (Read 1885 times)
nice guy
electrical question
« on: August 17, 2014, 09:04:20 pm »
   So I decided on a hot tub, Jacuzzi 345 60 amp.  Now the wiring.  My wire run is 140 feet. I was going to run # 6 wire but the electrical guy from Lowes said I have to drop down a wire size because of the distance?  Is that true?
2nd question.  I was going to buy the lowes  disconnect with a 60 amp breaker and 2 120v slots. I was going to run 2 separate legs of 120 in separate conduit but put it in the same trench as the hot tub wire.  Does that all sound ok?  Thanks for any help.
electrical question
Re: electrical question
« Reply #1 on: August 18, 2014, 12:30:47 am »
 #6 is fine never heard of anyone running #5 The wire can all run in the same conduit 2 loads 120 each and one ground from the GFCI 4 wires from the main box.
buba
« Reply #2 on: August 18, 2014, 10:36:43 am »
140 ft is on the hairy edge of 6AWG for 60AMP. I think the Lowe's guy is giving you good advice, besides 4AWG THHN/THWN is only a few cents more per foot than 6AWG. If you go with 4AWG, be thinking 1 1/4 inch conduit to make the cable pull easier. No reason you could not put all the wire in a single larger conduit unless they are going off in significantly different directions. IE: all wire in one large conduit to the tub area and use a large weather tight box to direct the individual wires out to the final locations using smaller rigid or  flex conduit.
« Last Edit: August 18, 2014, 11:36:29 am by buba »
nice guy
« Reply #3 on: August 18, 2014, 06:19:36 pm »
Thanks, think i will run # 4 wire to the disconnect then # 6 to the tub.