Where my tub will be going, there is a 220v 50 amp outlet wired to my main panel(50' away) with 8-4 copper wire. I plan on switching the outlet to a disconnect box with a 50 amp gfci. This disconnect box will be about 10' from the tub. Should I use 6-4 from the disconnect to the spa? Or match the 8-4?
-
Mowin, 6 4 sounds good to me. I think, however, the disconnect should be not less than 5' from the tub. I'm sure others will chime in on this.
-
10' is not less than 5' ;-)
-
This information might be in your owners manual.
My jacuzzi reads: "When using wire larger than #6, add a junction box near the spa and reduce to short lengths of #8 wire to connect to the spa".