Welcome to our forum.
I like the therapy story with this system but am concerned about the energy consumption and the ampsthat it would take to operate all pumps, the heater, light, etc. at the same time. Systems with 2, 2.5 hp motors, 5.5 kw heater, light, etc. operates on a 50 amp circuit. Anything beyond the above, per the law of electricity, would have to have 60, 70, or even an 80amp system. As long as the customer knows this upfront and understands the need, not a big deal.
The Platinum class of spas have 3 HP (I believe that's break HP) motors and claim they draw 4.6 amps to operate. I read either here or on Doc's board that when all the pumps are on the heater is programed to shut down keeping the tub in it's 50 amp rating.
Mendo,The NEC requires that all circuits carry 80% of their rated capacity. So a 50 Amp circuit can carry around 40 amps so your calculations are correct.For the Artesian: 5 pumps x 4.6 amps each = 23 Amps and a 5.5 KW heater draws another 23 amps so it would be too high for a 50 amp circuit. I don't know why they don't up the requirements to 60 amps but all their 220 Volt tubs are 50 Amp.Vinny
I don't know why they don't up the requirements to 60 amps but all their 220 Volt tubs are 50 Amp.Vinny
The folks I have dealt with who didn't like the higher-amp option had all gotten very high bids on the electrical work.
Hmmm... Wonder why the electrical bids were higher? When we had ours done the electrician said it was the same price either way we went. The wiring was the same it was just a different breaker in the box.