With 2 2.5hp pumps running on high and the heater on, you are drawing somewhere around 48 amps. It will run on a 50amp breaker, but all the codes I have seen require the breaker to be sized 25% over what the rated load would be.
2 pumps on low and the heater running easily run on 50amps.