Author Topic: Electrical Install Questions  (Read 1637 times)

Nick_M

  • Junior Member
  • *
  • Posts: 7
Electrical Install Questions
« on: August 29, 2016, 02:32:23 pm »
In preparation for the new hot tub I just ordered, I will be doing some of the rough electrical work and a licensed electrician friend of mine will be doing the final terminations and inspect the work I did and thus I have 2 quesitons.

1) I understand that the GFCI disconnect box needs to be a minimum of 5' from the spa.  Does anyone know if there is any height requirement off the ground and also if there is any minimum distance from a hose bib?

2) Is there a requirement that that conduit needs to be metallic versus non-metallic.  I plan on using flexible conduit.

Thanks!

Hot Tub Forum

Electrical Install Questions
« on: August 29, 2016, 02:32:23 pm »

Tman122

  • Ultimate Member
  • *****
  • Posts: 4424
  • If it Ain't Broke
Re: Electrical Install Questions
« Reply #1 on: August 29, 2016, 07:45:20 pm »
I think these to questions are variable to your local code requirements. Minimum of 5 feet and within sight. I wouldn't install the gfci shut off any higher than you can comfortable reach for access and repair. I'm guessing the hose bib has close to the same requirement. 5'.
Retired

Hot Tub Forum

Re: Electrical Install Questions
« Reply #1 on: August 29, 2016, 07:45:20 pm »

 