Size of wire for my new hot tub question
« on: February 17, 2015, 08:06:13 pm »
I am replacing my hot tub which was using a 50amp circuit breaker to my Artesian Santa Cruz Spa. The current wire is 6awg and is being run for approx 36 feet. Is this sufficient, and all I need to do is change out the circuit breaker??

Hot Tub Forum

Size of wire for my new hot tub question
« on: February 17, 2015, 08:06:13 pm »

Tman122

  • Ultimate Member
  • *****
  • Posts: 4424
  • If it Ain't Broke
Re: Size of wire for my new hot tub question
« Reply #1 on: February 17, 2015, 10:39:56 pm »
Depends on your local codes but I think it's overkill in the NEC book.
Retired

flava flav

  • Junior Member
  • *
  • Posts: 22
Re: Size of wire for my new hot tub question
« Reply #2 on: February 18, 2015, 02:06:45 pm »
Talk to an electrician and read up on NEC 2011.  Double and triple check that it's 6 gage.   Also you need to check the amp draw from the tub.  You can put an 60A breaker on 6 gage copper romex wire.  Although romex 6 gage is rated for 55 amp NEC allows to round up on the breaker size.  If it's THHN wire than its rated for 65A. http://www.cerrowire.com/ampacity-charts   
I'm sure the tub will draw less than 55 amp.  As long as it does then it sounds like a breaker change to 60A will only be required while using the existing wire.  Good luck and be safe boyeee.

Hot Tub Forum

Re: Size of wire for my new hot tub question
« Reply #2 on: February 18, 2015, 02:06:45 pm »

 